Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features

Comment #1

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 3
Paragraph / Figure / Table / Note: 2
Comment Type: Technical

Comment:

The proposed amendment still includes ...

"If these spaces contain
terminal HVAC supply devices that provide less than 10 Btu/hour per square foot, or if
there is less than 15 CFM of supply air for every 100 square feet of floor area, these
spaces must not be included as conditioned floor area."


I would like to see an exception, that if the airflow is within 10% of Manual J, than the 15 CFM per 100 sq ft is not applicable.

 

Justification for Change:

We emphasize correct sizing and correct airflow but the tools that decide it are not referenced as an verification method.

I see many instances where the Manual J 8th Ed calls for less airflow in a basement. I have seen some reports showing 8CFM/100 sq ft was all that was req.

 

Proposed Change:

"If these spaces contain
terminal HVAC supply devices that provide less than 10 Btu/hour per square foot, or if
there is less than 15 CFM of supply air for every 100 square feet of floor area, these
spaces must not be included as conditioned floor area.

Exception, if the airflow is within 10% of Manual J, than the 15 CFM per 100 sq ft does not apply."


Comment #2

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 34-35
Paragraph / Figure / Table / Note: one
Comment Type: Technical

Comment:

Power flow hods are not the only devices used to measure ventilation. Non-powered Balometer should also be included in the perferred equipment. This seems to be favoring one manufactor over others.

Justification for Change:

Non-powered devices which have been used in commercial applications longer than residential.

Proposed Change:

I recommend reconsideration of this section on measuring ventilation.


Comment #3

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: All
Comment Type: General

Comment:

The procedural directive to measure/inspect/determine has been lost in translating the current Appendix A to this proposed language.  The "task" column in the table in current Appendix A directs the rater to measure/inspect/determine characteristics/performance of the building elements.  I recommend wholesale editing of this proposed language to reintroduce the original language directing raters to measure/inspect/determine.

Justification for Change:

Without appropriate language this normative Appendix does not sufficiently constitute on-site verification procedures needed to support the rating system.

Proposed Change:

Edit proposed amendment as appropriate to include language in "task" column of table in Appendix A in existing standard.


Comment #4

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 20
Comment Type: Technical

Comment:

Current Standard, including Appendix A, does list HVAC equipment rated output capacity as a minimum rated feature.  I recommend adding this to Appendix A.

Justification for Change:

The information is needed in 303.5.1.4.

Proposed Change:

Determine the rated output capacity of the space heating and cooling equipment.  This information may be collected from manufacturer's label afixed to the equipment or from the appropriate appliance directory from AHRI using the model number from label afxied to the equipment.


Comment #5

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 3
Comment Type: Editorial

Comment:

As written:

Measure the house or assembly element (window, wall, ceiling, etc.) to the nearest inch,
and record the square footage to the nearest square foot.

Justification for Change:

Rounding individual windows to nearest square foot might introduce higher than necessary rounding errors.

Proposed Change:

Measure the house or assembly element (window, wall, ceiling, etc.) to the nearest inch,
and record the total area for each type of element to the nearest square foot.


Comment #6

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 4
Comment Type: Editorial

Comment:

delete second paragraph (divide basement and crawl walls into above and below grade).

Justification for Change:

duplicates what has already been stated on previous page (3).

Proposed Change:

detete the paragraph "Note to divide basement and crawl space walls into above and below grade."
 


Comment #7

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 4
Comment Type: Editorial

Comment:

As written,

"Measure the area of the window or skylight openings to the nearest inch. Calculate the
area using the measured width multiplied by the height."

Justification for Change:

Make wording consistent wording with previous text. Also, the Standard requires window areas to be recorded by orientation.

Proposed Change:

Measure the area of the windows and skylights to the nearest inch, and record the total area for each orientation to the nearest foot.


Comment #8

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 5-10
Comment Type: Editorial

Comment:

numerous inappropriate language throughout the insulation and grading section:

"must require" (1 instance)

"must not require" (5 instances)

"must be permitted to" (5 instances)

"must not be permitted" (9 instances)

Justification for Change:

This wording is inappropriate for a standard.

Proposed Change:

must require => must have (1 instance)

must not require => is not required to have (5 instances)

must be permitted => must or may, depending on context (5 instances)

must not be permitted => are not allowed (9 instances)


Comment #9

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: numerous
Comment Type: Technical

Comment:

Pg. 2 paragraph 2: The statement "Conditioned floor area does not include spaces such as uninsulated basements or attics that are unfinished, if there is no intentional HVAC supply or if the HVAC supply is inadequate to be considered directly conditioned space according to the definition in Appendix B of these Standards" is misleading. This would seem to indicate that unfinished or uninsulated attics with supply air going to them would be allowed to be considered part of CFA, even though that is ridiculous. Attics should NEVER be part of CFA unless they are fully finished and conditioned living spaces. Thus, you need to differentiate from basements, wihch can be unfinished and uninsulated but still have the floor area counted as CFA such as in existing homes as the spaces are used as living area, from attics which are almost never used in this way and thus should never be part of CFA. You should also make a statement regarding crawlspaces never being part of CFA.

Pg 3 paragraph 2: This entire paragraph is really misleading. Once again, when did we start including attics and crawlspaces in CFA? My understanding is that CFA has a very specific purpose, which is to have the softwrae calculate sqft normalized cost and consumption parameters which simulate people living in a home. PEOPLE DO NOT LIVE IN ATTICS OR CRAWLSPACES. This is a real step in the wrong direction if you start to allow this because A) it is totally illogical and B) it will make logical people like me have the impossible job of explaining why crawlspaces and attics can be included in CFA during HERS courses when i know for a fact they should not. Thus, my opinion is that you cannot lump in basements, crawlspaces and attics all together in this. Basements are a different animal in which, due the prevelance of unfinished but conditioned basements in existing homes, it actually makes it easier to allow people to include them in CFA from a comprehension standpoint. With attics/crawls being included in this you are mucking up logic.

Pg 4: Shouldn't it mention that windows are measured using the RO dimension? You mention that the exterior of the frame is included for existing homes... but isnt this also true for new construction?

Pg 9:  With this new wording of insulation grading, there are only 3 categories: Perfect, less than perfect, nothing. To make GIII = uninsulated means you really only have two choices... GI and GII... this is a step in the wrong direction, as I think GIII should be a separate definition that is more similar to how it once was (ie 5% missing or whatnot). Also, how practical is it to have a separate guide for grading radiant barriers and reflective insulation? I just don't see the value.

Pg 14: The definitions of covered vs exposed don't make a lot of sense to me. Why would floors with a floor covering not be considered as having one? To me this is an erroneous distinction and should be scrapped.

Pg 28: For interior doors, conditoined space boundary should be referenced in Appendix B

Pg 28-: I don't see the value of repeating the informatoin contained in Chapter 8 here. Instead, Chapter 8 should simply be referenced.

Justification for Change:

I think the above are techincal flaws with the standard which should be reconsidred.

Proposed Change:

See above


Comment #10

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: all
Comment Type: General

Comment:

The document would be much easier to reference, teach from and share if there were a numbering system (e.g. A 1.1 would be Appendix A item 1.1).

 

Justification for Change:

ease of use

Proposed Change:

edit to have such a reference system


Comment #11

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 40
Comment Type: Technical

Comment:

Requires testing of direct or power vented combustion appliances at the termination.  This can often terminate at the roof thus requiring testing on the roof.  Direct or power vented combustion appliances are less of a concern for testing of CO since they don't rely on indoor (occupant) air for combustion.  More of a concern is when a sealed unit is not gasketed for gas pentetrations.

Justification for Change:

Being on the roof puts HERS Raters (an endangered species) at much more risk.  Especially the moutain rater (higher risk endangerment) with snow and icy roofs. It also would increase the costs of insurance for some companies as insurance companies jack up the rates if a company policy allows for employees to go on roofs.

Proposed Change:

Consider exempting this requirement when the termination is at the roof.  In thise case the rater can check for ambient CO levels instead and inspect that the system is fully sealed with gaskets at the furnace cabinet.


Comment #12

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 39
Comment Type: Technical

Comment:

Standard says “When spillage occurs or CO exceeds the limits specified below in section 9” (on proposed page 39), but I don't see where section 9 exists and don’t see limits anywhere in Appendix A.

Justification for Change:

Need limits to apply Standard

Proposed Change:

Create CO Limits Chart


Comment #13

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 8
Comment Type: Technical

Comment:

Why does open cell SPF insulation allow for 1 inch variance from specified thickness for grade I, and closed cell 3/4 inch, while others are only allowed 1/2 inch voids?

Justification for Change:

Shouldn't they all insulation be graded by the same variance in thickness?

Proposed Change:

Provide explanation why SPF is allowed more flexibility or have all insulation thickness variance be the same regadless of type.


Comment #14

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 5
Comment Type: Editorial

Comment:

Batt insulation 2a---The way this is read it could be interpreted that attic kneewall insulation when "installed in an attic above a ceiling must not require an air barrier"...this is confusing and could be misread.  It should be written that "ceiling insulation with attic space above must not require an air barrier on the attic side".  to clarify this only applies to ceiling insualtion.

Justification for Change:

If I were playing devils advocate I could interpret the phrase "insulation installed in an attic above a ceiling" to be kneewall insulation that is in an "attic above a ceiling" would not require an air barrier, which is not the intent.

Proposed Change:

rephrase to clarify that this only applies to ceiling insulation not vertical attic kneewalls.


Comment #15

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 9
Paragraph / Figure / Table / Note: Grade 3
Comment Type: Technical

Comment:

Page 9, Grade 3 second paragraph---This section implies we must model grade 3 as uninsulated? I think the difference between grade 3 and uninsulated should be defined whereas if an install is less than grade 3, then that percentage of excess voids or compressed area should be modeled as uninsulated or as a different insulation level. am I looking at this wrong?

Justification for Change:

This could be misinterpreted that anything less than Grade 2 would be considered uninsulated which would be inaccurate.

Proposed Change:

The difference between grade 3 and uninsulated should be defined whereas if an install is less than grade 3, then that percentage of excess voids or compressed area should be naoted as uninsulated or at a different insulation level.


Comment #16

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: all
Comment Type: General

Comment:

•Why do we have two testing procedures in the standard? Shouldn't Appendix A just reference chapter 8 for each of these tests?

Justification for Change:

Consistency and elminate confusion with have testing standards in two different sections

Proposed Change:

Reference Chapter 8 for each of the tests required in Appendix A


Comment #17

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 5
Comment Type: Editorial

Comment:

2.a. "Insulation installed in attics above ceilings..."

Justification for Change:

as written, this exception could be construced as applying to knee walls, which it clearly should not

Proposed Change:

Insulation installed in attics on ceilings...
OR
Ceiling insulation below an attic...


Comment #18

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 6
Comment Type: Technical

Comment:

2.b. "Insulation installed under floors directly above an unvented crawl space must not require an air barrier on the exterior side."

Justification for Change:

since floors above unvented crawl are typically uninsulated, it's not clear whether this exception was meant to apply to vented crawls? (also, the phrase "must not require" further confuses the intent, as already noted in Comment #8)


Proposed Change:

unclear of intent so cannot propose new wording


Comment #19

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 6
Comment Type: Editorial

Comment:

6.a. "Insulation installed in attics and ceilings must require an air barrier on the exterior or interior side."

6.b. "Insulation installed under floors that is directly above an unvented crawl space must not require an air barrier on the exterior side."

Justification for Change:

wording is confusing - exception 6.a. same as Comment #17, exception 6.b., same as Comment #18

Proposed Change:

see comment #17, #18



Comment #20

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 9-13
Comment Type: Technical

Comment:

As written, the new sections on insulation grading stipulate that Grade 3 insulation be modeled as uninsulated. This defeats the purpose of having a Grade 3 category! Also, the Standard makes it clear that only those areas that fail to meet Grade 3 installation criteria should be modeled as uninsulated, not the entire assembly, as currently written in the amendment.

The new sections on reflective / radiant insulation appear to define 2 grading categories, with Grade 3 being superfluous. If the intent is to not give credit for areas with less than 90% coverage, then only 2 grades should be defined.

A minor point: Standard refers to Grades I, II, and III, whereas amendment refers to Grades 1, 2 and 3.

Justification for Change:

References to Grade 3 being modeled as uninsulated are conflict with Section 303.4.1.4.2,

Proposed Change:

rewrite insulation grading sections to be consistent with Standard.


Comment #21

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 11
Comment Type: Editorial

Comment:

3. Exception: Nonstandard cavity widths.

Face-stapled reflective insulation should be cut to fit non-standard cavity widths. No exception is necessary since bullet 3 already stipulates that it must match the cavity width.

Justification for Change:

exception is unnecessary

Proposed Change:

delete exception for nonstandard cavity widths


Comment #22

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 13
Comment Type: Editorial

Comment:

Framed Floors section does not address floors over unconditioned crawls and basements.

 

Justification for Change:

correct an omission

Proposed Change:

add paragraph that addresses floors over unconditioned crawls and basements


Comment #23

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 22
Comment Type: General

Comment:

Confusing description:

Ground source heat pumps - are coupled to the ground through the use of a water well sometimes the same well as used for domestic water (known as "open loop" which water or a water/antifreeze mixture is circulated (known as "closed loop").

Justification for Change:

This paragraph is poorly written. No need to mention that some open loop GSHP's use the domestic water well.

Proposed Change:

Ground source heat pumps are coupled to the ground through a closed loop of horizontal or vertical tubing or through an open loop drawing water from a water well.


Comment #24

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 22
Comment Type: General

Comment:

Ductless split heat pumps and air conditioners are missing from list of HVAC types.

 

Justification for Change:

see comment above

Proposed Change:

Ductless air source heat pump - a split or packaged air source heat pump or air conditioner designed to be installed without an air distribution system. May provide heating and cooling, or cooling only.


Comment #25

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 25
Comment Type: Technical

Comment:

The section on instantaneous water heaters refers to RE (recovery efficiency) instead of EF. The Standard requires rater to record the EF factor (as evidenced by Table 303.8.1(4), which provides a default EF for instantaneous water heaters).

Justification for Change:

This omission is a carry forward from current version of Appendix A

Proposed Change:

Check the unit's nameplate for EF or look up the EF rating in an appropriate efficiency rating directory. If the EF rating is not listed in the directory, use the appropriate default from Table 303..8.1(4).


Comment #26

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 25
Comment Type: Editorial

Comment:

Final 3 paragraphs of Instantaneous Water Heaters appear to be applicable to all water heaters. The 3rd pf these paragraphs should simply be deleted since distribution losses are not currently addressed in Chapter 3 (not reflected in the equations).

Justification for Change:

Editorial change.

Delete superfluous information not currently addressed in Standard.

Proposed Change:

Move the following two paragraphs from page 25 to page 23, just below the main Domestic Water Heating header:

Visually determine if the water heater is wrapped with exterior insulation. If so, measure
thickness of the wrap and determine R-value.

Determine whether water heater is located in conditioned or unconditioned space.

 

Delete this paragraph:

Determine whether pipe insulation is installed on all 3/4" or larger, non-recirculating hot
water mains. Measure thickness of insulation and identify material to determine R-value.


Comment #27

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 26
Comment Type: Technical

Comment:

Section of Solar Water Heating is missing information on backup heat.

Justification for Change:

backup heat for solar water heater must be modeled

Proposed Change:

Add the following paragraph to section on Solar Water Heating:

Determine type of backup heat (typically an integrated electric element in the solar storage tank but may be a separate water heater).


Comment #28

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 27
Comment Type: Editorial

Comment:

Under Appliance section, the paragraph on clothes washers inadvertently refers to clothes dryers in four places.

Justification for Change:

editorial correction

Proposed Change:

Change references to 'clothes dryer' to 'clothes washer' in third paragraph on page 27.


Comment #29

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 29-30
Comment Type: Editorial

Comment:

In the Air Leakage section, bullets under Single Point Test are numbered incorrectly.

 

Justification for Change:

editorial correction

Proposed Change:

renumber bullets beginning at the bottom of page 29, starting from #1.


Comment #30

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 31
Comment Type: Technical

Comment:

The 4th paragraph in Duct Leakage section indicates circumstances when no duct leakage test is required. Since the RESNET Standard is used by some programs that require a total leakage test regardless of leakage to the outside, it would be sufficient to simply specify the conditions for which ducts may be assumed to have no leakage to outside.

Justification for Change:

Potential conflict with programs that require total duct leakage testing.

Proposed Change:

When ducts are in conditioned space with 100% of the system visible and the system is
fully ducted (i.e., no building cavities are used to transport air), the ducts may be assumed to have no leakage to outside the conditioned space.


Comment #31

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 31
Comment Type: Technical

Comment:

The 4th paragraph under Duct Leakage section specifies that 100% of ducts must be visible. This often requires a judgement call and, as such, has generated lively discussion in the LinkedIn RESNET BPI forum. It would be helpful to clarify the intent of the "100% visible" requirement. For example, is it to ensure rater doesn't miss an obvious leak (although the Standard doesn't stipulate any duct system inspection), or is it because leaks from visible ducts are considered less consequential than leaks from hiddle ducts? For example, it's not clear if this requirement would be satisfied, or not, if ducts were visible at time of leakage test (e.g., at rough-in), but hidden after drywall is installed.

Justification for Change:

clarification of intent for the 100% visible requirement

Proposed Change:

add appropriate modifications and conforming changes to Section 803.2


Comment #32

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 34-35
Comment Type: Technical

Comment:

Under Ventilation Airflow Settings, the sections on measuring flows into and out of grilles needs to be rewritten so as not to be specific to fan assisted flow meters.
 

Justification for Change:

Non-powered flow hoods are far more common than powered flow hoods. Non-powered hoods can be used to measure air flow rates in the expected ranges for most ventilation systems with adequate accuracy.


 

Proposed Change:

Rewrite initial paragraph(s) of each section (Flows into grilles, Flows out of grilles) so that either powered or non-powered flow hoods may be used.


Comment #33

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 2
Paragraph / Figure / Table / Note: 8
Comment Type: Technical

Comment:

 For the definition of "Conditioned, directly" suggest adding an attic option.

Justification for Change:

 The definition for Conditioned, Directly does not include an attic option, while the other definitions do. To maintain consistency across definitions, recommend adding the attic scenario.


Comment #34

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 2
Paragraph / Figure / Table / Note: 8
Comment Type: Technical

Comment:

 For the definition of "Conditioned, directly" suggest deleting the words "or unintentionally".

Justification for Change:

 Examples given here are for intentional conditioning.


Comment #35

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 3
Paragraph / Figure / Table / Note: 2, 4
Comment Type: Technical

Comment:

Suggest changing basement/unvented crawlspace designations from Unconditioned, Conditioned- Indirectly, and Conditioned Directly to Unconditioned, Semi-Conditioned and Conditioned.

 

Justification for Change:

Unvented Crawlspaces/Basements may have ducts to temper them or act as a drying mechanism. These spaces are not designed to reach the set-point of the thermostat and sometimes do not have intentional returns. These spaces are semi-conditioned and should be treated as such in the calculations. Semi-Conditioned should include all basements/unvented crawlspaces with wall insulation that are indirectly or directly heated/cooled, but are not designed to reach the set-point.

 

Proposed Change:

 Change unvented crawlspaces/basements to have the following classifications: 1. Unconditioned- do not include volume/floor area in calculations 2. Semi-conditioned- do not include in volume/conditioned floor area 3. Conditioned- Keep wording same as "Conditioned, directly"


Comment #36

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 4
Paragraph / Figure / Table / Note: 2
Comment Type: Technical

Comment:

Delete "Note to divide basement and crawl…"

 

Justification for Change:

Already mentioned on Page 3.

 


Comment #37

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 5
Paragraph / Figure / Table / Note: 2 (Item 5)
Comment Type: Editorial

Comment:

Suggest changing "filled" to "fill"

 

Justification for Change:

Grammatical change


Comment #38

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 5
Paragraph / Figure / Table / Note: 2 (Item 5)
Comment Type: Technical

Comment:

Suggest removing "substantial"

 

Justification for Change:

There should be no gaps or voids. The word "substantial" is too vague.

 


Comment #39

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 6
Paragraph / Figure / Table / Note: Item #2b
Comment Type: Technical

Comment:

Suggest removing "unvented"

 

Justification for Change:

Should apply to all crawl space types, vented and unvented.

 


Comment #40

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 6
Paragraph / Figure / Table / Note: Batt Insulation Item #3
Comment Type: Technical

Comment:

#4- Faced Staple Style batts should not be allowed to be side stapled unless required by code.

 

Justification for Change:

Side stapling causes compression and is not required by code throughout the country. If a faced batt is required a non-staple product may be a better choice (friction fit faced batt).

 

Proposed Change:

 Should Read: #4 Side stapling is only allowed when required by code. When side stapled, compression is permitted only along edges to the depth of the stapling tab.


Comment #41

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 6
Paragraph / Figure / Table / Note: Batt Insulation Item #5
Comment Type: Technical

Comment:

Remove "substantial"

 

Justification for Change:

There should be no gaps or voids. The word "substantial" is too vague.

 


Comment #42

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 6
Paragraph / Figure / Table / Note: 3
Comment Type: Technical

Comment:

Blown Item #1- Fabric should be face stapled to studs.

 

Justification for Change:

Insulation will not be in contact with air barrier and cause thermal performance issues. If side stapling is required then a contractor will not use this product as cost will increase and thermal performance will decrease.

 


Comment #43

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 6
Paragraph / Figure / Table / Note: Blown Insulation Item #7
Comment Type: Technical

Comment:

Remove "substantial"

 

Justification for Change:

There should be no gaps or voids. The word "substantial" is too vague.

 


Comment #44

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 9
Paragraph / Figure / Table / Note: 4
Comment Type: Technical

Comment:

Remove "Grade 3 installations must be recorded and modeled as uninsulated."

 

Justification for Change:

Grade 3 insulation still provides some insulation value and should be counted as such. In addition, there could be potential problems with deemed savings programs. If you count Grade III as uninsulated, then deemed savings will be drastically overestimated.

 


Comment #45

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 9
Paragraph / Figure / Table / Note: 5
Comment Type: Technical

Comment:

For Items #2 and #4, add something to include the gaps and cracks around SIP panels (e.g. connections to floor systems)

 

Justification for Change:

Air leakage at connection between floor system and SIP panels is not addressed.

 


Comment #46

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 10
Paragraph / Figure / Table / Note: 2
Comment Type: Technical

Comment:

Grade 3 - Suggest removing "Grade 3 installations must be recorded and modeled as uninsulated."

 

Justification for Change:

Grade 3 insulation still provides some insulation value and should be counted as such. In addition, there could be potential problems with deemed savings programs. If you count Grade III as uninsulated, then deemed savings will be drastically overestimated.

 


Comment #47

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 11
Paragraph / Figure / Table / Note: Grade 3
Comment Type: Technical

Comment:

Grade 3 - Suggest removing "Grade 3 installations must be recorded and modeled as uninsulated."

 

Justification for Change:

Grade 3 insulation still provides some insulation value and should be counted as such. In addition, there could be potential problems with deemed savings programs. If you count Grade III as uninsulated, then deemed savings will be drastically overestimated.

 


Comment #48

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 12
Paragraph / Figure / Table / Note: Grade 1, Item #2
Comment Type: Technical

Comment:

After "2% or less of the roof", propose adding "or gable walls." Add note that radiant barriers on gable walls shouldn't disturb attic ventilation. Comment also applies to Grade 2, Item #1.

 

Justification for Change:

There is research to suggest adding radiant barriers to gable walls to improve performance.

 


Comment #49

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 12
Paragraph / Figure / Table / Note: Grade 3
Comment Type: Technical

Comment:

Grade 3 - Suggest removing "Grade 3 installations must be recorded and modeled as uninsulated."

 

Justification for Change:

Grade 3 insulation still provides some insulation value and should be counted as such. In addition, there could be potential problems with deemed savings programs. If you count Grade III as uninsulated, then deemed savings will be drastically overestimated.

 


Comment #50

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 12
Paragraph / Figure / Table / Note: IRCCs
Comment Type: Technical

Comment:

Propose adding the word "thermal" before emittance in first line of this section.

 

Justification for Change:

Typically this material is rated in terms of thermal emittance by the industry.

 


Comment #51

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 12
Paragraph / Figure / Table / Note: IRCCs
Comment Type: Technical

Comment:

RB Method 1 addresses vapor permeability by requiring the material be perforated. As with RB Method 1, this material too needs to address vapor permeability.

 

Justification for Change:

Need to address vapor permeability for this material.

 


Comment #52

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 12
Paragraph / Figure / Table / Note: IRCCs #3
Comment Type: Technical

Comment:

Recommend removing #3. "The coating must be dry to the touch."

 

Justification for Change:

This requirement should be part of the manufacturer's instructions for installation. This item is not specified for any of the other liquid applied products.

 


Comment #53

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 14
Paragraph / Figure / Table / Note: 3
Comment Type: Technical

Comment:

Delete this sentence: The insulation used is generally fiberglass batts, often folded in an L-shape and attached to the rim joist.

 

Justification for Change:

Ineffective insulation technique. Batts be should cut to fit cavity.

 


Comment #54

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 15
Paragraph / Figure / Table / Note: 8
Comment Type: Technical

Comment:

Use a stud finder.

 

Justification for Change:

Difficult technique. Most people cannot locate a stud by knocking.

 


Comment #55

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 21
Paragraph / Figure / Table / Note: 10
Comment Type: Technical

Comment:

Use the model numbers to look up efficiency in a directory such as AHRI or by using manufacturers data.

 

Justification for Change:

Nameplates may not give the accurate efficiency for split systems and for other cases.

 


Comment #56

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 27
Paragraph / Figure / Table / Note: 3
Comment Type: Technical

Comment:

Recommend separating dryer information from washer information.

 

Justification for Change:

Unclear


Comment #57

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 27
Paragraph / Figure / Table / Note: 6
Comment Type: Technical

Comment:

Recommend adding "sewer gases" to "Potential airborne contaminants such as fireplace ash, mold or asbestos."

 

Justification for Change:

Sewer gases are a common indoor air quality concern.

 


Comment #58

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 28
Paragraph / Figure / Table / Note: 2
Comment Type: Technical

Comment:

Open garage door when conducting blower door test.

 

Justification for Change:

From a house leakage, IAQ, and combustion safety standpoint, we recommend keeping the garage door open while conducting the blower door test. You want to make sure you are testing the wall separating the house from the garage. We want to test the air barrier between the house and garage. In addition, you should be testing the air barrier that is aligned with the thermal envelope.

 


Comment #59

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 31
Paragraph / Figure / Table / Note: 6
Comment Type: Technical

Comment:

Delete paragraph

 

Justification for Change:

Ducts need to always be tested regardless if they are entirely in the conditioned space in order to ensure comfort and Energy Star compliance

 


Comment #60

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 31
Paragraph / Figure / Table / Note: 9
Comment Type: Technical

Comment:

Motorized dampers should not be closed

 

Justification for Change:

We want to test the entire duct system. Not just part of the system. If the dampers are closed you will be eliminating part of the system (zoned system or supply ventilation).

 


Comment #61

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 32
Paragraph / Figure / Table / Note: 11
Comment Type: Technical

Comment:

Duct system pressure should be measured with reference to outside.

 

Justification for Change:

Measuring to inside the building may give you an inaccurate test depending on duct location.

 


Comment #62

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 35
Paragraph / Figure / Table / Note: 9
Comment Type: Technical

Comment:

What about other methods for testing airflow? (Applies to flows both in and out of vents). Recommend defining accuracy of equipment. +/- a % or a set CFM which ever is less.

 

Justification for Change:

Should define an accuracy range that is required. This will allow other equipment to be used.

 


Comment #63

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 35
Paragraph / Figure / Table / Note: 9
Comment Type: Technical

Comment:

Remove "Open a window or door to the outside."

Justification for Change:

Having the window open is not a worst case test for ambient CO in the space during oven operation.


Comment #64

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 2
Paragraph / Figure / Table / Note: Conditioned, direclty
Comment Type: Technical

Comment:

If we are defining directly conditioned space that is intentionally conditioned by means of a forced air heating or cooling system, hydronic heat, electric resistance, etc, then it is not "unintentionally" conditioned.

Justification for Change:

Clarity

Proposed Change:

Remove "unintentionally"


Comment #65

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 4
Paragraph / Figure / Table / Note: #3
Comment Type: Technical

Comment:

No air spaces "must be allowed" between different insulation types or systems.  This is a poorly worded sentence and sounds like a sloppy translation into English.  It can be made more direct and concise.

Justification for Change:

Clarity

Proposed Change:

Reword to:  No air spaces between different insulation types or systems.


Comment #66

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 5
Paragraph / Figure / Table / Note: Insulated Sheathing #5
Comment Type: Editorial

Comment:

"Sheathing joints must be 'durable' taped..."

Is durable tape the same type of tape as duck tape?

Justification for Change:

Clarity

Proposed Change:

Replace "durable" with "durably".


Comment #67

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 5
Paragraph / Figure / Table / Note: Batt insulation #a
Comment Type: Editorial

Comment:

"Insulation installed in attics above ceilings 'must not require' an air barrier on the exterior side."  This is a poorly worded sentence and typical of the sentences that follow it.

Justification for Change:

Clarity

Proposed Change:

Reword to:  An air barrier is not required on the exterior side of insulation installed in attics above ceilings.


Comment #68

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 6
Paragraph / Figure / Table / Note: Batt insulation #b
Comment Type: Editorial

Comment:

"Insulation installed under floors directly above an unvented crawl space 'must not require' and air barrier on the exterior side."  Another poor translation into English.  Are we trying to say that if you have a vented crawlspace it must have an air barrier on the exterior side?

Justification for Change:

clarity

Proposed Change:

Reword to:  An air barrier is not required on the exterior side of insulation installed under floors directly above an unvented crawl space, vented crawl space, or unconditioned basement.


Comment #69

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 6
Paragraph / Figure / Table / Note: Batt insulation #c
Comment Type: Editorial

Comment:

Poorly worded:  Insulation installed in rim or band joists located in condtioned space 'must not require' an air barrier on the interior side. 

Justification for Change:

Clarity

Proposed Change:

Reword to:  An air barrier on the interior side is not required for insulation installed in rim or band joists located in conditioned space.


Comment #70

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 6
Paragraph / Figure / Table / Note: Batt Insulation #3
Comment Type: Editorial

Comment:

Another poorly worded couple of sentences.

Justification for Change:

Conciseness and Clarity

Proposed Change:

Reword to:  Faced batts must be stapled to the face of the studs or side stapled to the studs with no buckling of the stapling tabs or be left unstapled.  Tabless batts and friction fit products do not require stapling.


Comment #71

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 6
Paragraph / Figure / Table / Note: Blown or Sprayed Loose Fill Insulation #a
Comment Type: Technical

Comment:

Poorly worded and contradictory to the Batt insulation requirements.  If batt insulation is not required to have an air barrier on the exterior side, why would loose fill insulation be required to have an air barrier on the exterior side?

Justification for Change:

Clarity

Proposed Change:

Reword to:  An air barrier on the interior side is required for insulation installed in attics and ceilings.


Comment #72

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 6
Paragraph / Figure / Table / Note: Blown... #b
Comment Type: Technical

Comment:

Poorly worded

Justification for Change:

Clarity

Proposed Change:

Reword to:  An air barrier on the exterior side is not required for insulation installed in floors that is directly above an unvented crawl space, vented crawl space or unconditioned basement.


Comment #73

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 6
Paragraph / Figure / Table / Note: Blown....#6c
Comment Type: Editorial

Comment:

Poorly worded

Justification for Change:

Clarity

Proposed Change:

Reword to:  An air barrier is not required on the interior side of insulation installed in rim or band joists located in conditioned space.


Comment #74

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 7
Paragraph / Figure / Table / Note: Open cell...#3
Comment Type: Editorial

Comment:

Poorly worded

Justification for Change:

Clarity

Proposed Change:

Reword to:  SPF insulation is considered an air barrier if it is installed in contact with the substrate and at a minimum thickness to be air impermeable per ASTM E283 or E2178.


Comment #75

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 7
Paragraph / Figure / Table / Note: Open cell...#5
Comment Type: Technical

Comment:

This contradicts #4 before it.  Is this sentence trying to say that you cannot fill the cavity to the face of the studs?  #4 is looking for the insulation to contact the interior sheathing, but #5 is looking for the sheathing to stand 1/2 inch away from the insulation.  Is the intention to keep the installed thickness of open cell SPF to at least 1/2 inch less than the stud cavity depth and preferably to the face of the studs for full contact with the interior sheathing?

Justification for Change:

Clarity

Proposed Change:

Reword to:  Open Cell SPF cavity insulation fill depth must be no greater than 1/2 inch from the face of the studs.


Comment #76

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 7
Paragraph / Figure / Table / Note: Closed cell SPF #3
Comment Type: Editorial

Comment:

Poorly worded

Justification for Change:

Clarity

Proposed Change:

Reword to:  Closed cell SPF insulation is considered to be an air barrier when installed in contact with the substrate at a thickness of at least 1.5 inches.


Comment #77

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 7
Paragraph / Figure / Table / Note: Insulation Grading
Comment Type: Technical

Comment:

Pictures are needed to demonstrate the Grading constraints similar to the current Appendix A.

Justification for Change:

A picture is worth a thousand words.  It is easier to perform a visual comparison of the standard to the insulation you are looking at than to visualize what the standard is saying and then looking at the insulation in the house to compare it to your visualization.

Proposed Change:

Create Graded renderings similar to the current Appendix A with enough words in the caption to correctly correspond to the worded standard.


Comment #78

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: all
Comment Type: General

Comment:

It is unfortunate that the amendment was published without indicating changes in strikeout/underline mode, leaving commenters to comb through the entire document in 30 days to determine what has changed. 

Proposed Change:

In the future please post amendments to major sections in strikeout/underline mode for review.


Comment #79

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 5 & 6
Comment Type: Technical

Comment:

On page 5 of the proposed document, in exceptions a, b and c change the word “must” to “shall.”

Justification for Change:

Item 2 exception a, currently states, “Insulation installed in attics above ceilings must not require an air barrier on the exterior side.” As proposed this language would not allow an air barrier to be installed on the exterior side of the insulation.

The language should permit the practice – but not mandate it. Changing the exception to say, “Insulation installed in attics above ceilings shall not be required to have an air barrier on the exterior side ” accomplishes this objective. This language allows attic insulation to be installed without an air barrier on the exterior side (as is typical for loose-fill insulation installed on attic floors) but the language does not prohibit installing an air barrier.

Changing “shall” to “must” in the exceptions b and c has the same effect of prohibiting the practice – not just allowing it to not be done and does not significantly affect the performance of the insulation.
 

Proposed Change:

Batt Insulation:

1. Insulation must fill the cavity being insulated side to side, top to bottom.
2. Insulation must be enclosed on all six sides.
(revise exceptions as shown)

Exceptions:
a. Insulation installed in attics above ceilings shall not be required to have an air
barrier on the exterior side.
b. Insulation installed under floors directly above an unvented crawl
space shall not be required to have an air barrier on the exterior side.
c. Insulation installed in rim or band joists located in conditioned space
must not be required to have an air barrier on the interior side.
d. (remains unchanged)
 


Comment #80

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: All
Paragraph / Figure / Table / Note: All
Comment Type: General

Comment:

It appears that the proposed amendment eliminates all the illustrations in Appendix A. In the version of proposed changes to this appendix that were circulated to the technical committee circa January 2010 (none of which were incorporated here) the illustrations were not removed.

Justification for Change:

Although the illustrations are not complete and there may be many that are lacking, it is helpful for many people to visualize with pictures rather than words.

Proposed Change:

 Please reinstate the illustrations in the appropriate places.


Comment #81

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 7 & 8
Comment Type: Technical

Comment:

On pages 7 and 8 under the Grade 1 criteria for batts are addressed. Installing batt insulation under floors is typically done using wire supports. In order for these supports to hold batts within the floor cavity and firmly up against the floor sheathing it requires some force. This force would likely compress the batt more than ½” maximum required for Grade 1 in the area where it contacts the batt. For this reason NAIMA recommends allowing a ¾” compression for Grade 1 batts installed under floors.

Justification for Change:

Allowing a ¾” compression with wire supports for under floor insuation would allow insulation to be held firmly in palce and have negligible the energy performance of the home.

Proposed Change:

(add new exception to Grade 1 criteria for Batts or Loose-fill section)
Exception: Batts installed under floors using wire supports shall not be compressed more than ¾ inch of the nominal insulation thickness.
 


Comment #82

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: n/a
Comment Type: General

Comment:

The current draft does not contain any guidance on how to grade hybrid insulation systems. For example how does one grade a wall which is partially filled with spray foam and the remainder filled with loose-fill or batt insulation? These systems are becoming more widely used and the RESNET appendix should contain guidance on how to grade those systems.

Justification for Change:

Raters need guidance on grading hybrid systems.

Proposed Change:

Add language stating that hybrid systems be graded by their individual components and the overall grade should be the lowest of the individual components.


Comment #83

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: all
Comment Type: General

Comment:

Consider an editorial review of the proposed language and changing the word “must” to “shall” in most cases. This is the commonly accepted term used in building codes and standards and will make the document more acceptable to the building code enforcement community.


Comment #84

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 7
Paragraph / Figure / Table / Note: Batt and Loose-fill insulation
Comment Type: Technical

Comment:

The first sentence allows up to 2% gaps or voids, but the second sentence says that voids are not allowed.  If the intent is to only allow compression or lack of thickness to a certain degree, then the words gap and void should not be used as they denote an area that is completely missing insulation.  Webster defines void as "containing nothing"

Justification for Change:

Clarity, if we want cavities to be fully insulated, top to bottom, side to side with no voids, then do not say you allow voids then say that you do not allow voids.  Keep in mind that the Rater is evaluating the insulation installation, not performing the insulation installation, unless he fills out the RESNET standard disclosure stating so.

Proposed Change:

Reword to:  When evaluating batt, or loose fill insulation, no more than 2% of the total insulated area (cavity) must be compressed more than 1/2 inch of the nominal thickness in any given location.  Voids are not permitted.

 


Comment #85

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 2
Paragraph / Figure / Table / Note: 4th paragraph
Comment Type: Technical

Comment:

The description "This is because the ambient temperature of the space is close to the outdoor ambient temperature or higher (in the case of attics in the
cooling season)." is unnecesasry and confusing.

Justification for Change:

This content isn't needed in normative standard. 

Proposed Change:

Delete the sentence


Comment #86

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 2
Paragraph / Figure / Table / Note: 5th paragraph
Comment Type: Editorial

Comment:

 "An unvented crawl space, basement or attic may be considered either unconditioned, indirectly conditioned, or fully conditioned, based on the following criteria:"; "fully condtioned" is not defined in the standard or in the following secitons.  

Justification for Change:

 Keep terminology consistent with definitions.

Proposed Change:

 Change "fully" to "directly"


Comment #87

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 2
Paragraph / Figure / Table / Note: 7th paragraph
Comment Type: Technical

Comment:

Criteria and examples for indirectly conditioned are confusing and inconsistent with the definition of "indirectly conditioned".

Justification for Change:

Make the language consistent with the long-standing definition of indirectly conditioned space.

Proposed Change:

Replace the paragraph with the following: "Conditioned, indirectly - In an indirectly conditioned space, heating and/or cooling is delivered to the space either through wall, floor, or ceiling assemblies, or by losses/gains from the heating/cooling system. An indirectly conditioned space typically lacks a functional thermostat. Indirectly conditioned spaces are considered conditioned space for the purposes of a rating. Indirectly conditioned spaces may be intentional or unintentional. Examples include a finished room that does not have distribution equipment or terminal devices; an unvented attic with large air leakage communication to the home; a vented or unvented attic with higher levels of insulation in the roof than in the attic floor and significant air leakage to conditioned space; a basement or crawlspace with higher levels of insulation in the exterior walls than in the ceiling; a basement, crawlspace, or other buffer space with uninsulated or unsealed mechanical equipment and/or HVAC distribution equipment. Indirectly conditioned spaces are typically between the temperature of the indoor conditioned space temperature and the outdoor ambient temperature.


Comment #88

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 8
Paragraph / Figure / Table / Note: Open-Cell PSF...
Comment Type: Technical

Comment:

This section is poorly worded and seems contradictory.  Are voids allowed or not?  The average thickness must be greater than the specified thickness but not less than 1 inch below the specified thickness or more than 3/4 inch below the specified thickness....If open cell SPF's R-value per inch is similar to fiberglass batts, why is its compression standard different?

Justification for Change:

Clarity, since we are looking at Grade I in this section, make it easy.

Proposed Change:

Reword this section to:  No more than 2% of the insulated area must be more than 3/4 inch below the specified thickness.  Voids are not permitted.


Comment #89

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 2
Paragraph / Figure / Table / Note: last paragraph
Comment Type: Technical

Comment:

 Conditioned space description is confusing and inconsistent with the definition. It also uses the term "fully conditioned" which is not defined. 

Justification for Change:

Eliminate confusing cross-references and eliminate inconsistency of terminology and definitions.

Proposed Change:

Replace section as follows: "Conditioned, directly - In a directly conditioned space, heating and/or cooling is delivered to the space by intentional distribution equipment and/or terminal devices, and are typically maintained at the same or similar temperature as other above grade finished spaces.  

In some cases, in may be necessary to interview the owner about the temperature in the basement or attic during the heating and cooling seasons, and assess the potential for standby loss from the heating equipment and distribution system, e.g., jacket insulation, leakiness of ducts, insulation on distribution systems, etc.

If basement, crawl space or attic is determined to be directly or indirectly conditioned, its walls and floor (for basement or crawlspace) or roofline (for attic) are considered part of the conditioned space boundary.  In those cases, the floor between the house's ground floor and the conditioned basement or crawl space, or the ceiling between a conditioned attic and the conditioned space below is considered an interior boundary with no associated heat transfer.

Determine volume of conditioned and indirectly conditioned space by multiplying floor area by ceiling height. The house may need to be split into different spaces with different ceiling heights and added to each other for both conditioned and indirectly conditioned spaces. For areas with vaulted ceilings or other irregular shapes, volume must be calculated geometrically."


Comment #90

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 8
Paragraph / Figure / Table / Note: Closed cell SPF
Comment Type: Technical

Comment:

Same type of confusion in this section as the open cell section. 

Justification for Change:

Clarity

Proposed Change:

Reword to:  No more than 2% of the insulated area must be more than 1/2 inch below the specified thickness. Voids are not permitted.


 


Comment #91

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 8
Paragraph / Figure / Table / Note: Grade 2 batt
Comment Type: Technical

Comment:

Are voids allowed or not?  If voids are not allowed, do not say you can have 15% voids.

Justification for Change:

Clarity

Proposed Change:

Reword the section:  No more than 15% of the total insulated area (cavity) must be compressed more than 3/4 inch of the nominal insulation thickness in any given location.  Voids are not permitted.


Comment #92

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 9
Paragraph / Figure / Table / Note: Open cell SPF
Comment Type: Technical

Comment:

same poor wording as batt and loose fill section

Justification for Change:

Clarity

Proposed Change:

Reword to:  No more than 15% of the insulated area must be more than 1 inch below the specified thickness.  Voids are not permitted.


Comment #93

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 9
Paragraph / Figure / Table / Note: closed cell spf
Comment Type: Technical

Comment:

same comments as open cell section above

Justification for Change:

Clarity

Proposed Change:

Reword section:  No more than 15% of the insulated area must be 1/2 inch below the specified thickness.  Voids are not permitted.


Comment #94

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 4-13
Paragraph / Figure / Table / Note: Insulation/grading
Comment Type: Technical

Comment:

(Note: this comment spans general, technical, and editorial.) This entire section as re-written seems to describe best practice requirements for new installations (whether new construction or new retrofits to be inspected), but is not useful for raters who are evaluating existing insulation.  This was a shortcoming of the previous language in this section, but the new language has moved firmly in that direction.  At a time when RESNET is trying to improve its image andreinforce the relevance of HERS ratings to existing homes and retrofits, and when other parts of the standard (air and duct leakage testing, and savings calculation proceduces for existing home retrofits) have been enhanced to reinforce and support that distinction, it is unfortunate to see this insulation grading section move in the opposite direction.  The original intent of the grading system was primarily to provide a punitive--but not extreme--categorical guideline for inspecting and modeling less-than-ideal insulation installations, so as to provide an incentive for builders and installers to follow manufacturer's guidelines and widely accepted industry practices.   There is language intended to convey that the use of grading is more discretionary for existing home installations, but that language was not consistent and many raters seem to believe that typical performance of a batt-insulated wall that was previously built would actually be represented well by Grade III, which in reality is likely to be too conservative.  Conservative (in terms of predicting higher energy use) is good in a new work/compliance environment, but is counterproductive in assessing existing homes for retrofit work, because it leads to overestimating savings potential.   

Justification for Change:

Continue to enhance RESNET's ongoing efforts to provide relevant distinctions between ratings used for compliance/new work/new construction and ratings used to assess existing home retrofits, rather than inhibit those efforts.

Proposed Change:

I will register a number of separate, specific changes that support this objective.

Also note that the use of arabic numerals "1, 2 and 3" for the grades is inconsistent with the section on insulation grading in Section 303.4.1.4.  If arabic numerals are to be used, that section must be amended correspondingly; I believe that specific change would editorial and could be made without further public comment process.


Comment #95

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 9
Paragraph / Figure / Table / Note: Grade 3
Comment Type: General

Comment:

Modeling Grade 3 insulation as uninsulated is an unfair penalty.  The modeling should reflect the conditions present.  More than 15% of the area compressed 1/2 to 1 inch is not an uninsulated space.  The insulation R-value in those areas is reduced by the amount of compression or lack of fill and should be modeled at that R-value.

Justification for Change:

A confirmed rating is supposed to model what is present and can be modeled with R-value per inch tables and compression tables instead of defaulting to an R-0.

Proposed Change:

Allow modeling the Grade 3 areas using R-value per inch or R-value based on compression tables.


Comment #96

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 9
Paragraph / Figure / Table / Note: SIPs #2 and 4
Comment Type: Technical

Comment:

The Structural Insulated Panel Association does not require that gaps and penetrationsss must be air-sealed with expanding foam.  Why is RESNET requiring this? 

From the SIPA website: 

"Voids
All voids must be filled with appropriate sealants/panel adhesives manufactured to ensure against air movement and moisture intrusion into the building envelope."

Justification for Change:

RESNET should not dictate specific products when the manufacturing association it sites does not.

Proposed Change:

Reword using similar language as found on the SIPA website. 

Delete number 2 and roll it into 4

All gaps and penetrations through SIPs including windows, doors, and foundation or roof connections must be air-sealed with appropriate sealants/panel adhesives manufactured to ensure agains air movement and moisture intrusion into the building envelope per the SIPA website.


Comment #97

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: Page 4
Paragraph / Figure / Table / Note: Insulation: opening paragraph
Comment Type: Technical

Comment:

The original language of the insulation grading section contained the phrase ""When it is possible to inspect insulation as installed (i.e., new construction)".  The insulation grading system was created more to create a strong incentive in a new work, that is "inspectable", for installers to follow industry-standard techniques.  It was never intended to be as punitive for existing home inspections, but the language indicating that was weak and unclear.

Justification for Change:

Enhance the distinction between inspections used for compliance purposes (new homes or new work inspections) and ones that are used to estimate existing home energy use for auditing or savings estimates.  

Proposed Change:

Delete the paragraph under the heading "Insulation" and replace with the following:

"For the purposes of compliance with new construction enengy codes, voluntary programs, or inspection of newly installed insulation retrofits, in order to meet the requirements of Grade 1 or Grade 2, insulation material must be installed according to the minimum general installation requirements, the minimum specific application requirements, and the minimum specific material requirements in this Appendix and the grading requirements for each type of insulation material.  

For the puropses of existing home energy audits or estimating existing home energy use for the purpose of savings estimates, Grade 2 shall be used as the default assumption for energy performance of any insulation, unless the installation is fully visible and a more detailed assessment is possible.  "


Comment #98

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 4
Paragraph / Figure / Table / Note: Minumum General Installation Requirements
Comment Type: Technical

Comment:

In item #2, the phrase "interior to and" conflicts with several of the specific application requirements below. 

Justification for Change:

The phrase is unnecessary, because the relationship to interior or exterior air barriers are detailed in each of the application requirements below.

Proposed Change:

 Delete "interior to and"


Comment #99

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 10
Paragraph / Figure / Table / Note: Grade 2
Comment Type: Technical

Comment:

Why has Grade 2 for SIPs been reduced from "standard" insulation's 15% defects to 2% to 5%?  Shouldn't insulation be graded similarly throughout the standard?  How deep into the insulation within a SIP panel are cutouts for electrical boxes, pipes and other penetrations going?  Is an electrical box or pipe penetration that has been sealed around a repaired area of damage and does not count towards the 2% to 5% allowable damage?

Justification for Change:

Clarity, with batt, blown or spray foam insulation, when electrical boxes and pipes are encountered and insulated behind and around, this is not counted against the installation grade.  Why are cutouts that are surrounded by insulation being counted against the SIP's grade?

Proposed Change:

Align the standard with the earlier sections.


Comment #100

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 4
Paragraph / Figure / Table / Note: Minumum General Installation Requirements
Comment Type: Technical

Comment:

In item #3, the prohibition on air spaces is extreme and does not accounnt for differences in performance from different situations (e.g. vented vs. unvented air space; whether the insulation layer(s) are or are not continuous).  While sensible for new construction/compliance, it should be limited to that situation and allow for rater judgement for as-is insulation for existing home audits/ savings estimates.  

Justification for Change:

For example: even a fully vented air space between wall sheathing and rigid insulation exterior to the air space does not entirely nullify the R-value of that rigid insulation layer. If it's 0F,  I'd rather be wearing a down jacket with the zipper open and some air space between me and the jacket, than wearing nothing at all.

Proposed Change:

Add another exception: "For audits or savings estimates of as-is insulation in existing homes, a vented air space between insulation layers shall result in the exterior layer R-value of no more than 50% of its "normal" R-value.  Unvented air spaces may be treated as reducing the exterior insulation layer to Grade 3, regardless of its other installed chararteristics."  

 


Comment #101

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 4
Paragraph / Figure / Table / Note: Minumum General Installation Requirements
Comment Type: Technical

Comment:

Item #4 does not recognize a reasonable course of action: to reduce the assumed "density and thickness" to that which results in a lower R-value.  That logic is implied on P 7 under open cell foam, #5, exception; but this logic should be explicit and extended to the general requirements.  

Justification for Change:

This language is typical of "minumum installation requirements" but not helpful for raters doing an assessment of an existing home with pre-existing insulation.

 

Proposed Change:

Add an exception for #4: "When the specific R-value is not required for compliance purposes, the R-value may be reduced to a value consistent with the actual density, thickness, or compression of the insulation material."

 


Comment #102

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 10
Paragraph / Figure / Table / Note: SIPs grade 3
Comment Type: Editorial

Comment:

Grade 3 must be modeled as uninsulated.  So, a house with 5+% defects that will perform tremendously better thermally and infiltration wise than a fiberglass insulated house with less than 15% defects must be modeled as uninsulated.  I guess those planning on building SIP homes should not have electricity, cable, internet, phones, indoor plumbing, or mini-splits on exterior walls to insure that there are not more than 5% cutouts for electrical boxex, pipes and other penetrations.

Justification for Change:

Align the insulation standards

Proposed Change:

Model Grade 3 sections at the R-value per inch for the SIP insulating materials.


Comment #103

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 5
Paragraph / Figure / Table / Note: Minimum Specific Material Requirements
Comment Type: Technical

Comment:

 This heading should be changed so that the scope/intent is clearer.

Justification for Change:

 Consistency with recommended distinction between compliance and as-is installation assessment by raters.

Proposed Change:

 Add a subtitel under the heading "Minimum Specific Material Requirements." as follows: "For the purpose compliance, the following criteria apply for new installations to achieve Grade 1 or 2. For the purpose of an energy audit or assessment of pre-existing installations for estimating savings, the following criteria apply in order to assign Grade 1 to the material."


Comment #104

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 14
Paragraph / Figure / Table / Note: Slab on Grade
Comment Type: Technical

Comment:

"To identify slab perimeter insulation, look for a protective coating above grade as opposed to the usual exposed slab edge at any conditioned space(s)." 

We do not see many monolithic pours in the North East.

Justification for Change:

Clarity

Proposed Change:

Reword this sentence:  To identify exterior slab insulation on a monolithic pour, look for a protective coating above grade as opposed to the usual exposed slab edge at any conditioned space(s).


Comment #105

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 15
Paragraph / Figure / Table / Note: above grade walls
Comment Type: Editorial

Comment:

"Check for insulation at plumbing outlet under sink or, 'in order of preference,'....Whose preference is this?  What if I want to look through the hole the dog chewed in the wall first....? 

Justification for Change:

remove opinions, if this is a safety issue, say that.

Proposed Change:

Remove "in order of preference"  if for safety, replace with, "in order of relative safety"


Comment #106

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 5
Paragraph / Figure / Table / Note: Insulated Sheathing
Comment Type: Technical

Comment:

Item 1.  The requirement to tape all edges and joints _may_ make sense as a Grade 1 requirement, but certainly not for Grade 2.  Grade 2 is defined in the modeling process in 303.4.1.4.2 as if there were "_no insulation R-value for 2% of the insulated surface area_".  The actual R-value penalty for not taping seams when insulatation boards are tightly fitted to each other should be an order of magnitude smaller than that, so assigning Grade 2 in that case sholud be highly conservative.  Also the taping requirement is inappropriate for assessing pre-existing installations.   Finally, taping is inappropriate for fibrous exterior rigid insulation.  

Justification for Change:

 There is no corresponding requirement to tape or seal pieces of cavity insulation to adjoining insulation or to adjacent framing in order to attain grade 1 or 2; only that it be in substantial contact.  Further, this requirement would be inappropriate for applications of rigid insulation on interior surfaces, 

Proposed Change:

 Change heading from "Insulated Sheathing" to "Continuous Rigid Insulation" and eliminate item #1.  Change "Sheathing" to "Insulation" in item #3.  Delete the second sentence under item #4 "Only the joints.... air sealed".  


Comment #107

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 5
Paragraph / Figure / Table / Note: Insulated Sheathing
Comment Type: Technical

Comment:

Item 5 is not relevant to the energy assessment of the building.

Justification for Change:

Specific non-energy requirements for new installation of products is inappropriate for a normative standard on inspection requirements for a HERS rating of "minimum rated features"

Proposed Change:

Delete item 5.


Comment #108

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 24-24
Paragraph / Figure / Table / Note: instantaneous water heaters
Comment Type: Technical

Comment:

The section above states to look up the EF rating, but the instantaneous section says to look at a nameplate for recovery efficiency.  Recovery efficiency is not used in the modeling software REM/Rate for instantaneous DHW, but Energy Factor is.

Justification for Change:

correct modeling mistakes

Proposed Change:

Add the same language to the instantaneous DHW section for EF as in the storage tank DHW with the reminder that a 92% adjustment is to be made until the software can catch up.


Comment #109

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: All
Comment Type: General

Comment:

I agree with the commenter that the language used throughout "Must" or "must not" as referencing insulation materials or installation practice is inappropriate and confusing.  It sounds like a best-practice standard for installers of insulation rather than guidance for a rater inspecting both new and pre-existing work. 

Proposed Change:

 Per the previous commenter, or similar.


Comment #110

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 27-41
Paragraph / Figure / Table / Note: Onsite testing
Comment Type: Editorial

Comment:

Chapter 8 was created for a reason.  The onsite testing section should be listed as such and given a reference to Chapter 8.  There is no reason to repeat Chapter 8 unless Chapter 8 will be deleted and incorporated into Appendix A.

Justification for Change:

There is no point to copying the Chapter 8 onsite testing protocols in Appendix A.

Proposed Change:

Reference Chapter 8, do not copy it.


Comment #111

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 20-25
Paragraph / Figure / Table / Note: Definitions
Comment Type: Editorial

Comment:

Appendix B is the definitions/glossary section and all definitions should be moved there.

Justification for Change:

There is no point in repeating sections.

Proposed Change:

Move the definitions to Appendix B


Comment #112

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 6
Paragraph / Figure / Table / Note: First list item #4
Comment Type: Technical

Comment:

 Side stapled batts, even when stapled according to this guidline, may result in too much compression to correctly qualify as Grade 1.  

Justification for Change:

 This needs to be changed for clarity and consistency with the other grading requirements.

Proposed Change:

 At the end of item #4, add the following sentence: "If the compression exeeds the total allowed for the cavity depth under "Insulation Grading: Grade 1", then Grade 2 must be assigned.  


Comment #113

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 6
Paragraph / Figure / Table / Note: Blown or Sprayed... item #1
Comment Type: Technical

Comment:

 Item 1; if containment fabric is installed such that insulation does not fill the cavity, the insulation R-value should be adjusted accordingly.  

Justification for Change:

 Again, this sounds like a best-practice installation guide for new work rather than guidance for raters to assess what actually exists.

Proposed Change:

Add the following at the end of the sentence: "; except that the insulation R-value may be reduced according to the actualy installed thickness."


Comment #114

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 6
Paragraph / Figure / Table / Note: #7 at end of page
Comment Type: Editorial

Comment:

 Item #7 should not be indented. 

Proposed Change:

 Correct formatting.


Comment #115

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 7
Paragraph / Figure / Table / Note: Open Cell _and_ Closed Cell, items #1
Comment Type: Technical

Comment:

 The installer training requirement is inappropriate for grading pre-exsting installations. It may be difficult to verify even for new installations, and (if the material othewise meets the installation criteria) should probably not be a requirement.

Justification for Change:

This requirement is appropriate for program guidance in a compliance situation, but is beyond the scope of raters assessment of energy performance.  

Proposed Change:

 Delete items #1 from both sections.  At the very minimum, establish this requirement as a pre-requisite for Grade 1 only and only for compliance purposes for both types of spray foam.


Comment #116

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 7
Paragraph / Figure / Table / Note: Open Cell ... insulation item #4
Comment Type: Technical

Comment:

This requirement is not relevant to energy performance that the raters are assessing.  

Justification for Change:

Limit the normative standard on assessing minimum rated features to those qualities that affect the energy performance.  

Proposed Change:

Delete item #4.  


Comment #117

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 7
Paragraph / Figure / Table / Note: Open Cell ... insulation item #5
Comment Type: Technical

Comment:

Even for new installations, the 1/2" limit is arbitrary and may conflict with legitimate designs.  

Justification for Change:

The requirement to fill the cavity to within 1/2" only applies if the intended R-value requires that level of fill.

Proposed Change:

Eliminate #5.  If a statement is made in the general requiremens allowing for assessing a lower R-value when installed insulation thickness dictates, this is unnecessary.


Comment #118

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 7 and elsewhere
Comment Type: General

Comment:

Please return pictures for insulation grading.  Appendix A's greatest value, from a training and enforcement perspective, is in clarifying application of the standards.  Pictures and examples are very important for clarifying technical standards.

The insulation grading pictures would be especially missed, but other pictures from throughout appendix A are also valuable.

When in doubt, add pictures.  Please don't eliminate them.

Justification for Change:

 Pictures are essential.

Proposed Change:

 Return pictures to Appendix A.  If the old illustrations are misaligned with new standards, then please amend the pictures and release them concurrently.


Comment #119

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 8
Paragraph / Figure / Table / Note: Insulation Grading guidance
Comment Type: Technical

Comment:

There's a contradiction between limitting  the percentage of voids (15% for grade 2) and the statement that "voids through interior to exterior of the intended insulation areas must not be permitted"

Assessing insulation installation quality requires being able to determine thresholds for modeling and other calculations.

As a worst case interpretation of the grading guidance listed, I might say that any insulation, installed in a cavity with voids extending from the interior to the exterior of the intended insulation, fails the criteria for grades 1 or 2, and as grade 3, it must be modeled as uninsulated.

Justification for Change:

 Insulation grading recommendations are internally inconsistent, with regard to voids.

Proposed Change:

 rewrite insulation grading language to give clear percentages for thresholds of gaps and/or compression for each level.

Modeling guidance must be consistent with chapter 3.


Comment #120

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 17
Paragraph / Figure / Table / Note: External Shade Screens
Comment Type: Editorial

Comment:

 Please clarify what sort of screen samples are used, and how they are rated, in determining the SC of the screen. Having guidance about how to rate screens, including references such as the ASHRAE transactions, can help the rater.

Justification for Change:

 This seems to be a legacy procedure that never got fleshed out.  Without more detail, it's hard to follow and hard to teach.

Proposed Change:

 Strike this section or provide clarifying tables and descriptions.


Comment #121

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 8
Paragraph / Figure / Table / Note: First paragraph
Comment Type: Technical

Comment:

"...must not be missing or compressed more than 1/2 inch of the nominal..."   Compression of more than 1/2" means something very different if the rated thickness is 3 1/2" vs 12".  As the requirements below for open- or closed-cell sprayed foam vary due to the differing range of R-value per inch of the materials, some adjustment should be made in this requirement for thicker installations.  

Justification for Change:

 For consistency in overall impact, thickness of batt or loose-fill should be accounted for in setting limits for compression or missing thickness.

Proposed Change:

 Change to "...missing or compressed more than 1/2 inch per 6 inches of the nominal..." 

 


Comment #122

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 7
Paragraph / Figure / Table / Note: subtitle under "Insulation Grading"
Comment Type: Editorial

Comment:

 Related to a previous comment: "Insulated Sheathing" is a sub-set of a range of rigid insulation applications.  Subtitle and subsections below should be changed accordingly.

Justification for Change:

For consistency and completeness, all rigid insulation applications should be included.

Proposed Change:

 Change "Insulated Sheathing" in subtitle and elsewhere within this section to "Rigid Insulation"


Comment #123

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 8
Paragraph / Figure / Table / Note: Open-Cell Polyurethane...
Comment Type: Technical

Comment:

The parenthetical phrase at end of section heading "(cavity not filled and not trimmed)" only applies to some of the subsequent paragraph.

Justification for Change:

 Some of the requirements in this paragraph apply even if the insulation fills the cavity and has been trimmed.  The last two sentences apply in those cases, although the second-to-last sentence is arguably unnecessary due to the general requirements.

Proposed Change:

Delete parenthetical phrase in heading.  Replace paragraph with: "When assessing open-cell polyurethane spray foam that does not fill the cavity, the average of all thickness measurements must be greater than the specified thickness required to obtain the specified R-value. No more than 2% of the insulated area must contain voids or be more than ¾ inch below the specified thickness. The minimum installed thickness must not be
less than 1 inch below the specified thickness any point, or the R-value shall be adjusted to reflect less thickness. In all open-cell spray foam installations, voids extending from the interior to the exterior of the intended insulation areas must not be permitted."

 


Comment #124

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 8
Paragraph / Figure / Table / Note: Insulated Sheathing
Comment Type: Technical

Comment:

 Besides changing the section heading to "Rigid Insulation" as previously noted, the statement that installaitons need to meet the other requirements above is unnecessary, and inconsistent with the other sections above and below.  

Justification for Change:

 The minimum specific material requirements are stated previously in the insulation assessment section immediately previous, and don't need to be referenced here.

Proposed Change:

 Delete the first sentence "Insulated sheathing... requirements above". 


Comment #125

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 8-9
Paragraph / Figure / Table / Note: Grade 2 (Moderate Defects)
Comment Type: Technical

Comment:

The statement that "Voids through interior to exterior of the intended insulation areas must not be permitted." as stated, is inappropriate in this section.   This occurs at the end of each of the three separate sub paragraphs (batt/loose, open cell, and closed cell).

 

Justification for Change:

 The statement is inconsistent with the intent of the grading system and is in conflict with the modeling requirements in seciton 303.4.1.4.2. that Grade II (2) be modeled "...such that there is no insulation R-value for 2% of the insulated surface area..."

Proposed Change:

 Change the final sentence in three places to: "Voids extending from the interior to the exterior of the intended insulation may not exceed 2% of the surface area. "


Comment #126

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 3 - 4
Paragraph / Figure / Table / Note: Measuring Building Components
Comment Type: Editorial

Comment:

This section of appendix A is inconsistent in language, procedure, and tone.

Paragraph 1 appears to be for measuring Conditioned Floor Area, and references ANSI Z765-2005, etc, but doesn't clarify that.

Paragraph 2 suggests that only conditioned basements and crawl spaces have their walls hand floors measured.

Paragraph 3 applies the same rule of outside measurements (exterior measurements, to the nearest linear inch, to the nearest square foot) to all components no matter what type, no matter how big.  Rounding errors could compound quickly on multiple windows using this method.  The use  of exterior measurements only, is inconsistent with the guidance for measuring walls in paragraph 6.

Paragraph 7 suggests a bizarre method of determining area of a ceiling using the measured perimeter.

Paragraph 8 ironically suggests that in some cases, it may be necessary to calculate dimensions geometrically.

Justification for Change:

 The Measuring Building Components section appears to be a distillation from the existing Appendix A, without editing for clarity or consistency.  As proposed, it is not helpful.

Proposed Change:

 Write a section on measuring building components from scratch.  I would be happy to serve on a subcommittee that is given that job.


Comment #127

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 9
Paragraph / Figure / Table / Note: Grade 3 (Substantial Defects)
Comment Type: Technical

Comment:

 This section is incomplete and inconsistent with the intent of the grading system, and is in conflict with section 303.4.1.4.2.

Justification for Change:

 The statement is inconsistent with the intent of the grading system and is in conflict with the modeling requirements in section 303.4.1.4.2. that Grade III (or 3) be modeled "...such that there is no insulation R-value for 5% of the insulated surface area...".  There is a tremendous difference between an insulated surface with 5% of the insulation missing, and a completely uninsulated surface.  If there is consensus that new installations that don't meet Grade 2 should simply not be tolerated, then that statement should be made specifically in connection with rating inspections for the purpose of compliance; however, I believe that such a determination should be at the discretion of the program author, sponsor, or code body and not by RESNET.  In any case, to assess performance of pre-existing insulation with significant voids and defects and model it reasonably, A blanket requirement that grade 3 is recorded and modeled "no insulation" would lead to significant over-estimation of existing home energy use, and gross over-prediction of savings, particularly from retrofitting insulation to that assembly.

Proposed Change:

 Delete existing section (2 sentences) and replace with the following:  "Installations not complying with the general installation and material requirements, and the requirements for Grade 1 or Grade 2 above must be considered a Grade 3 installation.  Voids extending from the interior to exterior of the intended insulation in excess of 5% do not meet the requirements of Grade 3; in such cases, the full area of uninsulated areas must be counted separately from the insulated areas, and recorded as uninsulated."


Comment #128

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 1-40
Paragraph / Figure / Table / Note: All
Comment Type: General

Comment:

 Consider proposing changed sections of appendix A, separately and individually.  This is one of the most valuable sections for a rater, and deserves to be a strong document throughout.  The specific changes to Chapter 8, the Conditioned Floor Area interpretation, new appliance minimum rated features, and possible insulation grading standards, are all good reasons for amending the relevant sections of the appendix.

However, this draws into focus the many parts that are not improved, and which deserve the attention.  Looking at the number of comments on various sections (and looking at all the specific paragraphs I think deserve comment, but that I don't have time for), I think delegating amendments for each of those sections is in order.

Proposing each section individually would make the reviewing process easier and more productive, I believe. 

Justification for Change:

 Amending the entire appendix is difficult and necessarily incomplete.

Proposed Change:

 Reject the proposed amendment, and amend specific sections as they are rewritten and re-edited.


Comment #129

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 9
Paragraph / Figure / Table / Note: entire section on SIP panels
Comment Type: Technical

Comment:

 This is more like a new construction specification than guidance for rater assessment. The criteria as stated may be difficult to inspect even for new installations, and are not useful for inspection of pre-existing SIP structures. 

Justification for Change:

The procedures need to provide guidance for raters assessing pre-existing structures.  The statement that Grade 3 Installations be recorded and modeled as uninsulated is impractical, inconsistent with section 303.4.1.4.2, and inappropriate for modeling of existing homes or developing savings estimates.

Proposed Change:

 At a minimum, remove the statement that Grade 3 Installations be recorded and modeled as uninsulated.  Also, make it clear that the criteria for Grade 1 and 2 are intended as applying to new construction and/or new installations.


Comment #130

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 10-11
Paragraph / Figure / Table / Note: Reflective Insulation
Comment Type: Technical

Comment:

For reflective products it must be made clear that insulation performance other than reflective air spaces per ASHRAE, or assemblies (per ASTM C1224), must be limited to the actual R-value of the material itself in accordance with standard R-vaule tests.  

Justification for Change:

 This can be confusing for raters, and it must be made clear that marketing claims of "equivalent R-value" can not be automaticalyl substituted for the R-value of "reflective" materials themselves.  Without clarification, it's not clear that the limitations from the previous section apply to the "reflective products" in this section.

Proposed Change:

Change item #7 to the following:  "The R-value for reflective insulation and radiant barriers installed in assemblies without an air space (for example, under slabs) shall be limited to the R-values of the material itself as tested per ASTM C518 or ASTM C177.  In general, these material R-values must be used unless assemblies meet the specific requirements for sealed air spaces (using R-vaules per ASHRAE Fundamentals) or entire assemblies (for assemblies rated in accordance with ASTM C1224) as stated above."


Comment #131

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 11
Paragraph / Figure / Table / Note: Reflective Insulation - item 5
Comment Type: Technical

Comment:

The performance of the product as a vapor retarder does not affect inspectors assessment of minimum rated features.

Justification for Change:

This normative appendix should be limited to guidance on minimum rated features as they affect energy performance. 

Proposed Change:

Delete the first sentence: "When reflective insulation is to serve as a vapor retarder... face-stapled."


Comment #132

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 11
Paragraph / Figure / Table / Note: Reflective Insulation - Grade 1-3 criteria
Comment Type: Technical

Comment:

The criteria for grade 1, 2 and 3 are far less stringent for radiant matierials than for insulation.  2% of area uninsulated (compared with 0% for insulation products) for grade 1; 2-10% missing insulation for grade 2.

Justification for Change:

The criteria shown are in direct conflict with the requirements above for reflective air spaces that "the enclosed airspaces must be sealed cavities which do not to allow air flow in out of the cavity" or " The assembly that is tested for thermal resistance must be representative of the field assembly".  

 

Proposed Change:

Set the grade 1 criteria to be "no gaps in the insulation are tolerated"; set the grade 2 criteria to allow no more than 2% gaps in reflective insulation.  Grade 3 should be limited to 5%, and the statement that grade 3 must be recorded and modeled as uninsulated should be deleted as per my previous comments.


Comment #133

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 12-13
Paragraph / Figure / Table / Note: Attic RBs and IRCCs
Comment Type: Technical

Comment:

The criteria for grade 1, 2 and 3 are far less stringent for radiant matierials than for insulation: 2% of area uninsulated (compared with 0% for insulation products) for grade 1; 3-10% and 2-10% missing insulation for grade 2, respectively.

Justification for Change:

These criteria shown are in direct conflict with the requirements above for reflective air spaces that "the enclosed airspaces must be sealed cavities which do not to allow air flow in out of the cavity"; or "The assembly that is tested for thermal resistance must be representative of the field assembly".  

Proposed Change:

In both sections, set the grade 1 criteria to be "no gaps in the insulation are tolerated"; set the grade 2 criteria to allow no more than 2% gaps in reflective insulation.  Grade 3 should be limited to 5%, and the statement that grade 3 must be recorded and modeled as uninsulated should be deleted as per my previous comments.


Comment #134

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 14
Paragraph / Figure / Table / Note: Slab on Grade "Covered" and "Exposed"
Comment Type: Technical

Comment:

The properties of "covered" and "exposed" are not defined anywhere in the rating standard, and no guidance as to the modeling of these properties is given.

Justification for Change:

 Allow software providers to define a range of floor coverings for slabs and model typical R-values for those materials, just as they do for other floors.

Proposed Change:

 Delete these two sections.  Add "Make a note of any floor finish or covering on the surface of the concrete slab."


Comment #135

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 17
Paragraph / Figure / Table / Note: Window glazing type - number of panes
Comment Type: Technical

Comment:

The second bullet "look at reflections" is incomplete.

Justification for Change:

 More guidance should be provided.

Proposed Change:

Change to: "Look at reflections from a slight angle with a pinpoint light source (a mini-mag light with the reflector removed iworks well). Double-paned windows will show four reflections (one for each surface of each pane)."


Comment #136

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 17
Paragraph / Figure / Table / Note: Window glazing type - tint or low-e coating
Comment Type: Technical

Comment:

The second bullet regarding the "match test" is incorrect and misleading.  Also evidence of field-applied window films should be added.

Justification for Change:

Low-e or tinted coatings do not add additional reflections; each pane of glass will show two reflections (one for each surface).  Suspended films may appear as an additional single reflection, but suspended films are not common.

Proposed Change:

Replace bullet item with: "Look at color of reflections with pinpoint light source: The color of a reflection from a glass surface with a low-e coating is typically different than the other surfaces. It may have a green, blue, orange tint compared with the others. Note that the low-e surface is always on the outer surface of the inside pane or the inner surface of the outside pane of glass."

Add bullet at end: "Look for signs of window-film application at edges of glass (peeling or imperfectly cut edges)."

 


Comment #137

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 18
Paragraph / Figure / Table / Note: Exterior shading
Comment Type: Technical

Comment:

 External shading may be important to avoid overestimating retrofit savings in existing homes.

Justification for Change:

 Provide better guidance for existing home assessments and energy savings estimates.

Proposed Change:

Add the following at end of section: "Note that external shading is excluded from the HERS index calculation but is important for retrofit savings estimates."

 


Comment #138

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 18
Paragraph / Figure / Table / Note: Doors
Comment Type: Technical

Comment:

Heat transfer test is inappropriate for determining door R-value

Justification for Change:

The final paragraph is misleading and impossible to apply in mild weather conditions.  The use of defaults is more appropriate than such a subjective test.

Proposed Change:

Delete the words "temperature transfer ," from the 2nd paragraph; delete the final paragraph "Heat transfer-...hollow door."


Comment #139

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 27-31
Paragraph / Figure / Table / Note: Air leakage testing
Comment Type: Technical

Comment:

 There are a number of inconsistencies between this section and section 802.2 of the standard.  It is not clear why this section does not simply reference 802.2; the idea that Appendix A could be used as a standalone document is difficult to justify considering the difficulties in maintaining two nearly identical, parallel sections within the same standard.

Under #3 Crawlspaces, #4 Attics, the terms "conditioned" and "unconditioned"are used ambiguously; in 802.2 the term used is "inside [outside] the conditioned space boundary" which is clear and well-defined in the standard.

In # 14 the treatment of evaporative coolers ("must be covered or sealed") conflicts with 802.2.13.

The final sentence after item #18 (dryers) is out of order and should be part of #10, though the language differs slightly from 802.2.9.

Beginning at the bottom of P29, the numbering is mixed up.

The statement at the bottom of p30 then refers readers to "the procedures in Chapter 8". this is inconsistent with the preceding section that mostly repeats section 202.2.

Justification for Change:

Sections 802.2, 802.5, 802.6 and 802.7 constitute inspection procedures and should be referenced in Appendix A.

Proposed Change:

 Delete the entire section and replace with a reference to Sections 802.2, 802.5, 802.6 and 802.7.  I think it's unnecessary, but if it is desired to repeat the sections so that Appendix A can be used as a standalone document, then these sections could be copied here, complete and "as-is", including section numbers (and indented or shaded to stand apart, with a note that they are repeated for the convenience of the user).


Comment #140

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 31 - 34
Paragraph / Figure / Table / Note: Duct leakage
Comment Type: Technical

Comment:

This secton repeats, almost verbatim, the requirements of 803.3-803.7, but without section numbers.  The difficulty in maintaining large sections of similar but not identical text in two areas of the standard is hard to justify, when a simple reference to the relevant sections would suffice.

Justification for Change:

Sections 803.3 - 803.7 constitute inspection procedures and should be referenced in Appendix A.

Proposed Change:

Delete the entire section and replace with a reference to Sections 803.3 - 803.7.  I think it's unnecessary, but if it is desired to repeat the sections so that Appendix A can be used as a standalone document, then these sections could be copied here, complete and "as-is", including section numbers (and indented or shaded to stand apart, with a note that they are repeated for the convenience of the user).


Comment #141

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 34
Paragraph / Figure / Table / Note: flows into grilles (section)
Comment Type: Technical

Comment:

Bag deflation method should be added to this section.

Justification for Change:

I have used the bag deflation method to measure air flows into grilles, and find it somewhat easier and more repeatable than the bag inflation method for air flows out of grilles.

Proposed Change:

 Add "bag deflation method" to this section (equivalent to the bag inflation method shown in the subequent section, but beginning with the bag full and measuring the time it takes to fully deflate.)


Comment #142

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 34
Paragraph / Figure / Table / Note: Ventilation Air Flow Testing
Comment Type: Technical

Comment:

 Some ventilation systems have dedicated pressure-measurement ports or accessories to allow "direct" measurement of air flows within the equipment or primary (trunk) ducts.  These systems should be noted and allowed as a measurement alternative.

Justification for Change:

 The use of manufacturer's instructions and accessories to measure air flow should be allowed.

Proposed Change:

 Add paragrah as follows to the opening section: "The use of dedicated pressure-measurement ports or accessories provided by ventilation equipment manufacturers to allow "direct" measurement of air flows within the equipment or primary (trunk) ducts may be used as an alternative to flow measurements at grilles.  Manufacturer's instructions shall be followed."


Comment #143

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 37
Paragraph / Figure / Table / Note: Comprehensive Home Energy Rating
Comment Type: Editorial

Comment:

The title of this section sholud be changed to "combustion appliance testing". 

Justification for Change:

 Other sections of the standard may indicate when these tests are required; those criteria need not be limited to a statement or section heading here.

Proposed Change:

Change the heading and opening paragraph to the following:

"Combustion Appliance Testing"  "If combustion appliance testing is required (such as for a Comprehensive Home Energy Rating) the following procedures shall be followed."


Comment #144

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 37-40
Paragraph / Figure / Table / Note: Combustion Appliance Tests
Comment Type: Technical

Comment:

This entire section duplicates sections 806-808 (but with inconsistencies).  Those sections should be mentioned here by reference, rather than repeated here (almost) verbatim.

 

Justification for Change:

Although already noted for the air leakage and duct test procedures, the difficulty in maintaning two separate but subsantially similar sections of the standard is far more obvious in this case.  Ironically, even while this Appendix is out for public comment, the technical committee is in the process of voting on a substantial revision to sections 806-809, which if adopted would necessitate re-writing and re-vetting this section of Appendix A.   A simple cross-refrence is much easier to promulgate and maintain.

 

Proposed Change:

Delete this section and refer to sections 806-808.  If necessary, provide an exact duplicate (including section numbers) set apart from the rest of the appendix A text with shading or an indent, and note that the section is repeated for the convenience of the user.  Such section would be automatically updated whenever the referenced sections were amended (and someone would need to remember to do that). 


Comment #145

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 4
Paragraph / Figure / Table / Note: 1
Comment Type: Technical

Comment:

Exterior Insulation 

“Minimum General Installation Requirements:

“2. Insulation must be integral to or interior to and in substantial and permanent contact with the primary air barrier.” (p. 4)


Insulation that is exterior to and in substantial and permanent contact with the primary air barrier should also be acceptable. For example, a floor over unconditioned space insulated with batts that are held against the subfloor by means of staves.

Justification for Change:

Exterior insulation is already permitted and the proposed language would contradict this.

Proposed Change:

 “2. Insulation must be integral to or interior to and in substantial and permanent contact with the primary air barrier, except for floor insulation in contact with an interior air barrier” (p. 4)


Comment #146

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 5
Paragraph / Figure / Table / Note: 1
Comment Type: Technical

Comment:

 Insulated floors


“Minimum Specific Application Requirements:


“1. Insulation installed in framed floor assemblies must be in substantial and permanent contact with the subfloor.” (p. 5)


The ENERGY STAR Homes program allows insulation to be installed at the exterior surface of the cavity under circumstances: “Fully-aligned air barriers may be installed at the exterior surface of the floor cavity in all Climate Zones if the insulation is installed in contact with this exterior air barrier and the perimeter rim and band joists of the floor cavity are also sealed and insulated to comply with the fully-aligned air barrier requirements for walls.” Can this allowance be explicitly added to the Appendix?

Justification for Change:

  Essentially, this alternate detail creates a “tub”-shaped insulation installation that should be equally effective with insulation that’s in contact with the subfloor. 

Proposed Change:

 “1. Insulation installed in framed floor assemblies must be in substantial and permanent contact with the subfloor or fully-aligned air barriers may be installed at the exterior surface of the floor cavity in all Climate Zones if the insulation is installed in contact with this exterior air barrier and the perimeter rim and band joists of the floor cavity are also sealed and insulated to comply with the fully-aligned air barrier requirements for walls.”


Comment #147

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 5
Paragraph / Figure / Table / Note: 1
Comment Type: Technical

Comment:

 
Baffling at eaves


“Air permeable insulation installed in ventilated attics and sloped roofs must have an effective air barrier (wind block, air chute, or eave baffle) installed at the eave or soffit edge that extends up and beyond the surface of the insulation or to the ridge vent to prevent air movement through the insulation.” (p. 5)


The ENERGY STAR Homes program allows air barriers to only be installed in bays that have soffit vents, as long as the air barrier is tabbed and prevents wind washing of adjacent bays. Can this allowance also be added to the Appendix?

Justification for Change:

 Wind baffles are primarily required where soffit vents are located. Tabbed baffles can prevent wind washing of adjacent bays.

Proposed Change:

 “Air permeable insulation installed in ventilated attics and sloped roofs must have an effective air barrier (wind block, air chute, or eave baffle) installed at each bay with an eave or soffit edge, or a tabbed baffle in each bay with a vent, that will also prevent wind washing of insulation in adjacent baysthat extends up and beyond the surface of the insulation or to the ridge vent to prevent air movement through the insulation.” (p. 5)


Comment #148

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: Throughout
Paragraph / Figure / Table / Note: Throught
Comment Type: Editorial

Comment:

 
“Must not require”


Throughout the proposed amendments, “Must not require” should be clarified. Does it mean that the treatment that follows is not required, but is permitted, or does it mean that what follows is prohibited? For example: “Insulation installed in attics above ceilings must not require an air barrier on the exterior side.”

Justification for Change:

 The intent of the phrase "must not require" is unclear.

Proposed Change:

 No proposed change suggested, becuase the intent of the current phrase is unclear.


Comment #149

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 10
Comment Type: General

Comment:

 SPF installer training


“Open cell spray polyurethane foam (SPF) insulation:


“1. Installers must meet the manufacturer’s recommended training requirements and must complete the online health and safety training for SPF provided by the Center for Polyurethanes Industry.”


“Closed-cell spray polyurethane foam (SPF) insulation:


“1. Installers must meet the manufacturer’s recommended training requirements and must complete the online health and safety training for SPF provided by the Center for Polyurethanes Industry.”


Will Raters be required to verify this as part of conducting a Rating? How? RESNET should not introduce a requirement that will not be recorded during a rating and that Raters will not be able to verify. It is recommended that RESNET remove this requirement or include it only as a recommendation.

Justification for Change:

 RESNET should not introduce a requirement that will not be recorded during a rating and that Raters will not be able to verify.

Proposed Change:

  It is recommended that RESNET remove this requirement or include it only as a recommendation.


Comment #150

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 7 and 11
Comment Type: Technical

Comment:

 
Reflective insulation in nonstandard cavity widths


p. 11: “Reflective Insulation in Ceilings, Walls and Floors:


“When face-stapled, the material width must match the framing width (e.g. 16” wide material is used for 16” on-center framing).


“Exception: Nonstandard cavity widths.” (p. 7)

RESNET should not exempt nonstandard cavity widths from this requirement. If the material width does not match the framing width, products will not be installed properly and will not perform as intended (or consistent with the test data or calculations used to determine the assembly’s R-value). If RESNET retains the exemption, RESNET should define “nonstandard”. Does it mean nonstandard with respect to a particular wall assembly, or to prevailing wall construction types in a market?

Justification for Change:

If the material width does not match the framing width, products will not be installed properly and will not perform as intended (or consistent with the test data or calculations used to determine the assembly’s R-value).

Proposed Change:

 Remove the exception or, if RESNET retains the exemption, RESNET should define “nonstandard”.


Comment #151

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 3
Comment Type: Editorial

Comment:

The 3rd paragraph on page 3 refers to a "fully conditioned" basement, crawl space or attic. Suggest changing to "directly conditioned"

Justification for Change:

consistent use of terminology

Proposed Change:

If basement, crawl space or attic is determined to be directly conditioned...


Comment #152

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: n/a
Comment Type: Technical

Comment:

Thermal resistance


Raters sometimes find it challenging to identify the correct thermal resistance of insulation materials for several reasons. First, manufacturers’ thermal performance claims are not always consistent. The R-value claimed for a product on a website or other marketing materials may be different from the R-value listed on the fact sheet (“tech sheet” or “spec sheet”) or the product packaging. The Federal Trade Commission has issued clear guidance on how thermal resistance claims must be made for insulation products (16 CFR Part 460). While the FTC can and does enforce these regulations, that enforcement occurs after violations have occurred; there is no body that reviews and approves manufacturers’ claims before their products are permitted to enter the market. The intensely competitive nature of the home insulation market, combined with some organizations’ limited ability to appropriately interpret and accurately characterize their products’ performance, leads to improper thermal performance claims.


Second, R-value claims may not be accurate. Marketers sometimes lack the technical ability to accurately interpret and convey test results or calculations in a way that enables Raters to determine whether or not the conditions of the testing are representative of those in the Rated homes or consistent with FTC labeling regulations. For example, manufacturers sometimes make “effective” or “performance” R-value claims based on the impact of characteristics other than resistance to heat flow, such as reduced air infiltration or thermal mass benefits. If these “performance” R-values are not clearly differentiated from (FTC-compliant) R-values, Raters may use them in their modeling, not knowing that they are overstating the actual thermal resistance or that thermal mass impacts vary by climate. As another example, sometimes the R-values claimed for reflective insulation products include the thermal resistance not only of the enclosed airspace, but of adjacent materials like OSB sheathing or drywall. When the materials included in the calculations are not clearly stated, Raters can inadvertently double-count the thermal resistance of layers when calculating an assembly’s U-value.


Third, Raters do not always use product-specific information. Some Raters rely on lists of typical insulation values for types of insulation materials that may be found in training materials, technical standards, rules of thumb transmitted through training, or default values listed in rating software.


Finally, Raters sometimes round R-values, for example deeming a product with an R-value of 2.6 to have an R-value of 3.


The proposed amendments to Appendix A will significantly improve the consistency and accuracy of Rater R-value determinations, especially for reflective insulation products. RESNET should refine the guidance for reflective insulation to more clearly convey where Raters should obtain R-value information, what information they should look for to be confident in its accuracy, and how to use those R-values in their calculations and ratings.


Determining Thermal Resistance for Reflective Insulation


Raters should obtain the R-values for reflective insulation materials from either the product packaging or from the product’s fact sheet. The Rater must verify that the R-value claim meets the following criteria:


1. It explains the number and thickness of air spaces that the claim is based on;
2. It explains the direction of heat flow that the claim is based on;
3. It is either based on calculations consistent with the 2009 ASHRAE Handbook of Fundamentals, or on testing consistent with ASTM C1224; and
4. If the R-value is less than R-10, it is rounded to the nearest tenth (e.g., R-1.6, no R-2).


Next, the Rater must use this information to verify that the number and thickness of the airspaces and the direction of heat flow in the rated home are consistent with those listed for the product. RESNET should clarify how Raters should account for heat flow. Manufacturer claims are based on one particular direction of heat flow, but in homes the direction of heat flow may change over the course of a year and even day, depending on the climate location. In the case of walls, heatflow should be considered horizontal, and the R-value will not vary by climate or season. There is some difference in the R-value that should be assigned to reflective insulation in attics (e.g., cathedralized ceilings, reflective chutes in rafter bays) based on the direction of heat flow, and there is a significant difference in floors.


Finally, when calculating and modeling, Raters should calculate R-values to the nearest tenth, and should take care to include only the benefits of the reflective insulation and air space in the rating software and not to double-count for other materials that may be referenced in promotional materials and/or already accounted for in the rating software (e.g., exterior air films, siding, OSB).


Determining Thermal Resistance for Mass Insulation


Raters should obtain the R-values for mass insulation materials from either the product packaging or from the product’s fact sheet. The Rater must verify that the R-value claim meets the following criteria:


1. It is accompanied by the details relevant to the performance of each type of material, adapted from 16 CFR § 460.12 and 16 CFR § 460.13, as follows:

  • Batts and blankets: R-value, thickness
  • Loose-fill insulation: Minimum settled thickness, initial installed thickness, maximum net coverage area, number of bags per 1,000 square feet, and minimum weight per square foot at R-values of 13, 19, 22, 30, 38, and 49.
  • Boardstock: R-value, thickness
  • Spray Polyurethane Foam: R-value at 3.5 inches

2. It is based on ASTM C518 or ASTM C177; and
3. If the R-value is less than R-10, it is rounded to the nearest tenth (e.g., R-1.6, no R-2).


When calculating and modeling, Raters should calculate R-values to the nearest tenth.

Justification for Change:

The proposed amendments to Appendix A will significantly improve the consistency and accuracy of Rater R-value determinations, especially for reflective insulation products. RESNET should refine the guidance for reflective insulation to more clearly convey where Raters should obtain R-value information, what information they should look for to be confident in its accuracy, and how to use those R-values in their calculations and ratings.

Proposed Change:

 Determining Thermal Resistance for Reflective Insulation


Raters should obtain the R-values for reflective insulation materials from either the product packaging or from the product’s fact sheet. The Rater must verify that the R-value claim meets the following criteria:


1. It explains the number and thickness of air spaces that the claim is based on;
2. It explains the direction of heat flow that the claim is based on;
3. It is either based on calculations consistent with the 2009 ASHRAE Handbook of Fundamentals, or on testing consistent with ASTM C1224; and
4. If the R-value is less than R-10, it is rounded to the nearest tenth (e.g., R-1.6, no R-2).

Next, the Rater must use this information to verify that the number and thickness of the airspaces and the direction of heat flow in the rated home are consistent with those listed for the product. RESNET should clarify how Raters should account for heat flow. Manufacturer claims are based on one particular direction of heat flow, but in homes the direction of heat flow may change over the course of a year and even day, depending on the climate location. In the case of walls, heatflow should be considered horizontal, and the R-value will not vary by climate or season. There is some difference in the R-value that should be assigned to reflective insulation in attics (e.g., cathedralized ceilings, reflective chutes in rafter bays) based on the direction of heat flow, and there is a significant difference in floors.


Finally, when calculating and modeling, Raters should calculate R-values to the nearest tenth, and should take care to include only the benefits of the reflective insulation and air space in the rating software and not to double-count for other materials that may be referenced in promotional materials and/or already accounted for in the rating software (e.g., exterior air films, siding, OSB).


Determining Thermal Resistance for Mass Insulation


Raters should obtain the R-values for mass insulation materials from either the product packaging or from the product’s fact sheet. The Rater must verify that the R-value claim meets the following criteria:


1. It is accompanied by the details relevant to the performance of each type of material, adapted from 16 CFR § 460.12 and 16 CFR § 460.13, as follows:

  • Batts and blankets: R-value, thickness
  • Loose-fill insulation: Minimum settled thickness, initial installed thickness, maximum net coverage area, number of bags per 1,000 square feet, and minimum weight per square foot at R-values of 13, 19, 22, 30, 38, and 49.
  • Boardstock: R-value, thickness
  • Spray Polyurethane Foam: R-value at 3.5 inches

2. It is based on ASTM C518 or ASTM C177; and
3. If the R-value is less than R-10, it is rounded to the nearest tenth (e.g., R-1.6, no R-2).


When calculating and modeling, Raters should calculate R-values to the nearest tenth.


Comment #153

Amendment: Proposed Amendment on On-Site Inspection Procedures for Minimum Rated Features
Page Number: 2
Comment Type: Technical

Comment:

The first section "Conditioned Space" primarily deals with Conditioned Floor Area. Suggest changing the section title to "Conditioned Floor Area".

Also, the explanations for Unconditioned, Indirectly Conditioned, and Directly Conditioned spaces are inconsistent with definitions given in Appendix B.

Justification for Change:

eliminate confusion in an area that is already very confusing

Proposed Change:

change section title to "Conditioned Floor Area", and rewrite explanations of unconditioned, indirectly conditioned and directly conditioned spaces so be consistent with definitions given in Appendix B